No need to do that. The size is based on the loads you are going to connect. If you are connecting all of the loads to the 1600 amp OCPD, then a 1600 amp ATS is fine.If the EMDB main breaker i.e ( 1600AT/2000AF) shall i use the ampere frame value as ATS AMP rating?
No need to do that. The size is based on the loads you are going to connect. If you are connecting all of the loads to the 1600 amp OCPD, then a 1600 amp ATS is fine.