My question concerns AFCI circuiting. Now that All general-use outlets in dwelling unit bedrooms rated at 125v 15 and 20A must be AFCI protected, Is it permissible to combine the receptacles and lights onto the same branch circuit? And if so, is it permissible to hit other rooms such as an adjoining bathroom from it?
I am new to the branch-circuit calculation part of this so i need help on how to calculate what exactly i can put onto a 15A AFCI circuit before it becomes "Full"
I realize that the 180VA per device only applies to Non-Dwelling applications, and that the bedroom receptacles are inluded in the 3VA per Sq. Ft. load calculations. 220-3(B)(10), 210-11(C)(3), and 210-52(E)&(G).
So with that said, when circuiting say a Master suite with master Bath, if i add up the maximum wattages of incandescent bulbs per each fixture 220-3(B)(4) , and the total computed load of ballasts on Flourescent fixtures 220-4(B) and the total is below 1,800 Watts (15A x 120v) then i am fine to place all remaining general-purpose receptacles on that circuit ?( in the master bedroom)
Theoretically i could have 1,799 Watts for the lights and 12 general-purpose receptacles all on 1 AFCI Breaker?
Do i apply 125% for this continuous load before determining if i am below the 1,800 Watts?
Correct me if i am off on this. If i have a 2,000 sq. ft. track home my general lighting load for a dwelling unit is 3VA per sq. ft. 2,000 x 3 = 6,000/120v=50amps\ (15a lighting circuits)= 3.33 round down to 3 (per 220.2(B) ). My minimum amount of lighting circuits for this house is 3 correct? Depending on the amount of Luminaires used and what type, i could use 3 AFCI breakers to protect every light and general-purpose receptacle in this house?
I appologize if this questions is way out of the ballpark. I need the all Information i can get.
Thank You.
Roger
I am new to the branch-circuit calculation part of this so i need help on how to calculate what exactly i can put onto a 15A AFCI circuit before it becomes "Full"
I realize that the 180VA per device only applies to Non-Dwelling applications, and that the bedroom receptacles are inluded in the 3VA per Sq. Ft. load calculations. 220-3(B)(10), 210-11(C)(3), and 210-52(E)&(G).
So with that said, when circuiting say a Master suite with master Bath, if i add up the maximum wattages of incandescent bulbs per each fixture 220-3(B)(4) , and the total computed load of ballasts on Flourescent fixtures 220-4(B) and the total is below 1,800 Watts (15A x 120v) then i am fine to place all remaining general-purpose receptacles on that circuit ?( in the master bedroom)
Theoretically i could have 1,799 Watts for the lights and 12 general-purpose receptacles all on 1 AFCI Breaker?
Do i apply 125% for this continuous load before determining if i am below the 1,800 Watts?
Correct me if i am off on this. If i have a 2,000 sq. ft. track home my general lighting load for a dwelling unit is 3VA per sq. ft. 2,000 x 3 = 6,000/120v=50amps\ (15a lighting circuits)= 3.33 round down to 3 (per 220.2(B) ). My minimum amount of lighting circuits for this house is 3 correct? Depending on the amount of Luminaires used and what type, i could use 3 AFCI breakers to protect every light and general-purpose receptacle in this house?
I appologize if this questions is way out of the ballpark. I need the all Information i can get.
Thank You.
Roger