What is the correct way to upsize the EGC when you add extra sets of wire to account for voltage drop? Please tell me if I’m doing it correctly in the example below.
The load being fed requires a 1600A circuit, which initially would require a 1600A breaker and (4) sets of (3) #600 CU & (1) #4/0 GRD. However, the feeder must be increased to (8) sets of #600 CU to meet voltage drop requirements.
Since the total area of the ungrounded conductors was doubled, the equipment grounding conductor must be doubled as well. So then, would the appropriate feeder be (8) sets of (3) #600 CU & (2) #4/0 GRD?
Or would you still use (1) #4/0 EGC per conduit, because the total area of all the EGCs is greater than (2) #4/0?