Here's the scenario,
We are providing power to run a irrigation pump with a phase convertor,
1. Utility is giving 480V. single phase at the road.
2. We must install underground cable 1650 ft. to phase -convertor/ pump location.We will be using aluminum direct buried cable. ( 60 -C.)
3. Phase convertor has a capacitor start. Starting amps. =55A.
4. Pump is located next to starter.
5. Pump is 480V. 3 PH. 20HP. FLA. 24.8. STARTING AMPS=119. ( Across the line start).
6. The convertor is designed to start 20 HP and run 40 HP.
7. I am having trouble calculating the voltage drop to size the underground cable, do I base it on the single phase load of 55 A. or the 3 phase load of 24.8 or a combination of the two?
We are doing more and more of these and do not want to undersize the feeder but also don't
want to be installing larger cable than needed. Thanks for any help available.
We are providing power to run a irrigation pump with a phase convertor,
1. Utility is giving 480V. single phase at the road.
2. We must install underground cable 1650 ft. to phase -convertor/ pump location.We will be using aluminum direct buried cable. ( 60 -C.)
3. Phase convertor has a capacitor start. Starting amps. =55A.
4. Pump is located next to starter.
5. Pump is 480V. 3 PH. 20HP. FLA. 24.8. STARTING AMPS=119. ( Across the line start).
6. The convertor is designed to start 20 HP and run 40 HP.
7. I am having trouble calculating the voltage drop to size the underground cable, do I base it on the single phase load of 55 A. or the 3 phase load of 24.8 or a combination of the two?
We are doing more and more of these and do not want to undersize the feeder but also don't
want to be installing larger cable than needed. Thanks for any help available.