How to find out if OCPD comply with 695.4 (B)(2)(a)(2)?
I think (d) is the easiest to verify, as long as the breaker is non-adjustable.
(a) and (c) should be checked using the Time-Current Characteristic (TCC) curve.
What about (b)? A re-start transient of 24 times the full-load current is a large number — but is there any specified time range?
695.4 (B)(2)(a)(2)
(2) Overcurrent protection shall be provided by an assembly listed for fire pump service and complying with the following:
a. The overcurrent protective device shall not open within 2 minutes at 600 percent of the full-load current of the fire pump motor(s).
b. The overcurrent protective device shall not open with a re-start transient of 24 times the full-load current of the fire pump motor(s).
c. The overcurrent protective device shall not open within 10 minutes at 300 percent of the full-load current of the fire pump motor(s).
d. The trip point for circuit breakers shall not be field adjustable.
I think (d) is the easiest to verify, as long as the breaker is non-adjustable.
(a) and (c) should be checked using the Time-Current Characteristic (TCC) curve.
What about (b)? A re-start transient of 24 times the full-load current is a large number — but is there any specified time range?
695.4 (B)(2)(a)(2)
(2) Overcurrent protection shall be provided by an assembly listed for fire pump service and complying with the following:
a. The overcurrent protective device shall not open within 2 minutes at 600 percent of the full-load current of the fire pump motor(s).
b. The overcurrent protective device shall not open with a re-start transient of 24 times the full-load current of the fire pump motor(s).
c. The overcurrent protective device shall not open within 10 minutes at 300 percent of the full-load current of the fire pump motor(s).
d. The trip point for circuit breakers shall not be field adjustable.