How to ground a service panel NOT!

Status
Not open for further replies.

sameguy

Senior Member
Location
New York
Occupation
Master Elec./JW retired
Need to see the service to see what's going on. From your picture I agree with the missed the water pipe by that much, 99!
 

kwired

Electron manager
Location
NE Nebraska
Is that raceway still bonded if you remove the bonding jumper in question?

May not be a grounding electrode but instead a bonding jumper for equipment grounding purposes.

May still need additional grounding electrode ran if there is none already.
 

480sparky

Senior Member
Location
Iowegia
Is that raceway still bonded if you remove the bonding jumper in question?

May not be a grounding electrode but instead a bonding jumper for equipment grounding purposes.

May still need additional grounding electrode ran if there is none already.

It's simply a bare ground from the panel to the conduit. The raceway goes directly to the panel. This is merely a redundant ground path. Does not attach to anything going to water pipe or electrode. I relocated it about 6" to the cold water pipe and verified the jumper at the meter.
 

kwired

Electron manager
Location
NE Nebraska
It's simply a bare ground from the panel to the conduit. The raceway goes directly to the panel. This is merely a redundant ground path. Does not attach to anything going to water pipe or electrode. I relocated it about 6" to the cold water pipe and verified the jumper at the meter.
Answered my questions I guess.
 