How to heat an electrical enclosure with -35 degree ambient temps?!?

Status
Not open for further replies.
That is the million dollar question. It don't take a lot of heat if all that is needed is to prevent condensation.

If something needs to be kept at a certain minimum it gets more complicated, plus you possibly even need to consider cooling abilities if there is a wide enough ambient temp swing.

I haven't checked all of the component spec sheets yet., but i have one that is a -5 min temp. so i have to keep it at least that warm

Condensation is not likely to be an issue at -35F. Air holds very little moisture at that temperature.

their spec sheet says 82% humidity in the winter (56% in summer)

LOL, if it's going to Russia just ship it and let Putin figure it out:):):):)

I agree! haha
 
Thanks for this information everyone. It helped me solve a far simpler problem here at home, where the lowest temp I
can expect is only about -5 F.
 
When you say motor starter, is it just a contactor/overload? Does that even need heating? Other than maybe a small electric heater to prevent condensation?
NEMA and UL standards for motor starters only require that they go down to 0C operation, nothing says it has to work below that. A-B 509 starters are rated down to -13C, Siemens to -5C, I couldn't find specs for any others. But -30 is way too cold to expect things to operate correctly and safely.

I've done panels for use in Prudhoe Bay Alaska at the oil fields, that's a similar environmental requirement. Their standard was to keep equipment between 0C and 40C. The 40C was NEVER a problem there, the warmest day I ever experienced there was 60F in the dead of summer... The 0C was the problem.
 
Just posting this info in case anyone finds it useful, ect...
This was the feedback I got from one of the big enclosure MFGR's

the software wouldn’t allow me to use any numbers for outside lower than 68 degrees F, so I rolled old school with the following calculation: Had to do come unit conversion so hopefully you can follow me.

Q h = A x k x (Ti – Tu) where: A is surface area 8.44 sqft = 0.784 m2 , k = heat transfer coefficient for carbon steel at 5.5 W/ m2 , in this case you have 0.784 m2 x 5.5 = 4.312W of thermal transfer. You have lowest ambient of -33 F and lowest internal at -5 F

Q h = 0.784 x 4.312 x (-5 – (-33))
Q h = 0.784 x 4.312 x (28)
Q h = 94.65 W

This says your minimum heat requirement is a minimum of 94.65 W. Now we add solar loading . For a gray box, you add 61-300W/ m2 in direct sunlight but this depends on factors like latitude, time of day and year, use of solar shields or double-wall constructions. Since it is so cold outside in this application, I would not count on any solar gain for this calculation in my opinion. If you want to take the 2W of load given in the info, you’re required heating would be a minimum of 92.65W.
By this calculation, I would recommend a 3105.360 (86-100w) or 3105.370 (130-150w) heater. A thermostat is recommended if you will have temperature swings or a hygrostat to maintain a specific humidity within the enclosure.
 