jbelectric777
Senior Member
- Location
- NJ/PA
Just show up on the job like ya know what yer talkn about..... lol, thats what i do, works for me. 
And, YES, a PV system IS considered a service!![]()
No, never a service, look at the definition of service in Artcile 100. Services are only provided by utilities.
I found the listing for the disconnect lugs today inside of the disconnect cover... they ARE multi-conductor lugs!
Same question applies to detached-building feeder discos.Why would they be required to be service rated if it's not a service?
Nah, it's just your imagination.Sometimes, I think I dream this stuff up!:-?
I was taken back by the 3rd picture. What's the deal with the "S" conduitors between disconnects? If they isolated them properly wouldn't that work, in respects to the lug size?
One each side, top to bottom, after I straighten that out, I released they had the wrong circuits in the wrong places...
Did they burn up anything? Your going to tell me they were just incorrectly labeled... :grin:
I think that may be correct for DC.
You double disconnect to minimize an arc under load.
I didn't really read all of the thread, so if someone already said it I apologize, but I would hope how many wires can be under the lug would be listed on the door of the disconnect.
I think that may be correct for DC.
You double disconnect to minimize an arc under load.
Originally Posted by cadpoint
I was taken back by the 3rd picture. What's the deal with the "S" conduitors between disconnects? If they isolated them properly wouldn't that work, in respects to the lug size?
One each side, top to bottom, after I straighten that out, I released they had the wrong circuits in the wrong places...
Did they burn up anything? Your going to tell me they were just incorrectly labeled...
What your looking at in picture three is one pole switched, not two pole switched per manufacture or our standing requirement to break all poles...
Minus the mislabeling of circuits it's Postive and Negative and not ungrounded and grounded.
With a DC array you will have grounded and ungrounded conductor, it can be positive or negative ground but one leg will be grounded.
As such we do not break the grounded conductor.
Yeah they should probably correct either the location or labeling of the grounded conductor.![]()