Have existing 1000KVA 480/277V 3ph padmount, underground feed to 1200A MCB Panelboard inside. Owner wants to subdivide the building into four tenants and wants 480/277 metered service to each. Utility Green book says 1000KVA 480/277 transformer has 18,100 A Fault Current. There are no EZ multi paks at 480. Though of wireway trough, with four Main CB/Meter Combos, can find them at 320A continuous and with 300 MCB but only at 10K AIC. All single meter sockets are rated 10K AIC. Though maybe fused disconnect upstream with current limiting fuses, but even with 300A CLF's the let through is around 12KA. The only other option is CT metering cabinet. But with four, 400AF/300A disconnects, four metering cabinetes, and four single socket meters, the space requirement is huge.
I can't find any manufacturer with meter sockets greater than 10KAIC. Can't use series rated, as the combo must be tested by manufacturer and nobody is making it.
While 1600A 208 3ph is easy with a MCB and Multi Pak, 1200A at 480V is very awkward.
Any ideas would be appreciated.
I can't find any manufacturer with meter sockets greater than 10KAIC. Can't use series rated, as the combo must be tested by manufacturer and nobody is making it.
While 1600A 208 3ph is easy with a MCB and Multi Pak, 1200A at 480V is very awkward.
Any ideas would be appreciated.