kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
My guess is said basement probably also has drainage tile, sump pump, fill near the wall is something that will drain easily, etc. and to a certain extent you don't really need a perfect seal.I disagree.
For reference, we just ran three 4 inch conduits into a basement 3' below the water table.
If you have the hole cored properly, and use a linkseal, combined with polywater fst foam, there will not be an issue.
https://www.polywater.com/product/polywater-fst-foam-duct-sealant/
http://www.cooperindustries.com/con...es/link-seal_environmentalsealforconduit.html