How to release some load in case there is the mains failure?
adindas
I have a switch boards which have got two supplies:
- Mains supply 800 KVA from utility company
- 500 Supply from standby Genset
There is Automatic mains failure (AMF). So in case there is a power failure, the generator is automatically kicking on.
But I have the following problem because my Genset can not take the full 800 KVA,
- I am aware that I could add Bus Couplers CB and divide it into essential/priority load and non essential/non priority load. And In case of power failure, the bus coupler will open and generator will only need to supply Essential load.
However, I do not want to do this as I prefer to do it by controlling the outgoing ways from the switchboards. So, In case there is a power failure, I will open some MCCBs which supply the non essential load. If the mains is restored, the MCCB shall manually/automatically be closed again. Is that any way to dot this?.
I have heard about put shunt trip, under voltage relay but do not how they work to solve this problem. Any advice will be greatly appreciated.
yes, you can use a shunt trip or undervoltage relay (27), however unless the breaker can be electronically closed after it is tripped, it would have to be manually reset.
Pierre; to that question you asked genrally no for few reason why is that most redentail dont have much room for motorized operator in the resdentail loadcentre unless have remote switching on the breaker
normally the motordriven opterators breakers useally found in med to large switchboard system but once a while smaller one too if added from factory option.