How to secure service mast on new construction?

letgomywago

Senior Member
Location
Washington state and Oregon coast
Occupation
residential electrician
Why are you telling him to go thru the wall. Standoff straps with #10 screws work just fine in brick or wood siding. The meter base and , as mentioned earlier, overhang will keep it from moving forward or even side to side.
He wanted a strong option. They can do vinyl j channel either side if he has a 4 inch piece of azek or something like that behind it and it'll work.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
The guy said vinyl siding is on the house. Just screwing straps or strut onto the wall is gonna smash the siding and make it look like crap.

@letgomywago said check utility specs, and that's accurate.

One POCO around here wants 2x4 blocks between the studs. Others may not care

I like to use either:
1) an offset nipple to get the mast tight to the siding, then use 2-hole straps.

or

2) minerallac straps so that I don't need the offset nipple.

In either case, if it's vinyl siding, I like to drill 7/8" holes for the screws, and use 1/2" PVC conduit sleeves, long enough to space from the sheath out to the face of the siding. And toggle bolts through the sheath (presuming no wood blocking)
Only time we have to use blocking is if it isn't going through the roof. Then we use an eyebolt and blocking if there isn't already some "meat" to screw into. Nuts and washers on the eyebolt on each side of the wall.
I use cut pieces of PVC too behind straps if needed.
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
This information might be helpful.
 

Attachments

  • Electrical Service Requirements (ESR) — 2022 Fourth Quarter Issue_Page_1.jpg
    Electrical Service Requirements (ESR) — 2022 Fourth Quarter Issue_Page_1.jpg
    155.4 KB · Views: 10
  • Electrical Service Requirements (ESR) — 2022 Fourth Quarter Issue_Page_2.jpg
    Electrical Service Requirements (ESR) — 2022 Fourth Quarter Issue_Page_2.jpg
    159.5 KB · Views: 10

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Some of our linemen get pleasure in "tension testing" the drops and I have seen decking & roof damage when they get overzealous.
If I couldn't get lag screws in the top plate I would normally use a piece of shallow strut fastened to the studs.
 