tryinghard said:Zog,
I bet you got this but I just want to add my reply to help.
?Overload? is different than ?Overcurrent? in the respect of Definitions. The breaker does provide overcurrent protection just specifically not overload protection. The overload protection for the motor and its branch circuit is provided by the OL?s or the thermo-protection on the motor.
The reason a breaker is sized at 250% is to allow startup (lock rotor), if it is sized too small it may trip. The equipment grounding conductor is sized from the OCP in Table 250.122 but it does not have to be larger than the phase conductor so #10 is fine for EGC on a 60A as well.
Thanks, got it, just not used to dedicated circuits, or breakers that dont have programable trips units or relays for shaping the desired Time/Current charteristics.