I have a project with a resistance welder that is 208v, 3 phase, 50A primary current. The circuit is fed by a local panel say PB1. The circuit supply conductor is sized not less that 70% of the rated primary current. 70%x50=35A, #8 wires. The branch circuit breaker is sized not more than 300% of primary current. 300%x50=150A circuit breaker.
The total connected load of panel PB1 is 80A. The main circuit breaker of the panel is 125%x80=100A. The feeder to the panel is #3 wires. Since the main circuit breaker is smaller than welder branch circuit breaker. In order to have good coordination, we have to increase the main circuit breaker and up stream circuit breaker to 150A. It results in that the feeder is not protected by any circuit breakers.
I am confused by the scenario. Could anybody explain it to me? Thanks.
The total connected load of panel PB1 is 80A. The main circuit breaker of the panel is 125%x80=100A. The feeder to the panel is #3 wires. Since the main circuit breaker is smaller than welder branch circuit breaker. In order to have good coordination, we have to increase the main circuit breaker and up stream circuit breaker to 150A. It results in that the feeder is not protected by any circuit breakers.
I am confused by the scenario. Could anybody explain it to me? Thanks.