J.P.
Senior Member
- Location
- United States
Another vote for pulling in new wire. Don't even bother megging it. You already know enough to have a reasonable concern that it is damaged.
We will be doing more than just mandrel tests, I assure you. In addition to brushing and swabbing the conduits, we will be visually inspecting all of them with a camera.I am sure you will do Mandrel test before you install the new conductors.
I agree. However, the contractor who did the installation will be financially liable for the repairs, and he's not going to agree to replacing all the wire unless we can prove that it's defective. Hence, the reason for this thread.Another vote for pulling in new wire. Don't even bother megging it. You already know enough to have a reasonable concern that it is damaged.
So we still need to come up with an acceptable test procedure for identifying how many damaged feeders we have. We do not want to simply pull them all out for visual inspection, because if a set of feeders are good, then we risk damaging them during the R&R. And the installation contractor is not going to take responsibility for redoing any work unless we can prove to him that actual damage exists.
I'd still like to hear any ideas on how to test these wires.