With only 1 or 2v across pool and ground with 1000V applied, the balance voltage must be dropped within your meter and so you are effectively applying 1 or 2 volts only.here is what i have done in the past to verify bonding on swimming pools. specifically wet niches.
1. shut off all power to pool.
2. take a fluke megger, i used the 1587, as it gives applied working voltage to the circuit under test.
3. tape one lead to a piece of pvc conduit.
4. attach the other lead to the pool ground.
5. stick lead on pvc pipe into pool, touching lead to pool light bezel.
megger @ 1000 volts between bezel on pool light, and earth ground.
6. you should read 0.0 megohms, as it should be a dead short.
7. however, your megger should also tell you how many volts it is maintaining
across the test circuit, and it'll be somewhere between 1 and 1,050 or so,
depending on the specific fluke you are testing with.
8. you should only see 1 or 2 volts displayed.
summary:
with 1000 volts applied to the pool, there is a difference of potential of only
one or two volts between the pool water, and the earth. this means the pool
light is correctly bonded.
it also means that a person perfectly grounded, sticking their hand in the pool
water when it became energized with 1,000 volts, might be subject to a 1 or 2
volt shock.
over the years, i've had three AHJ's agree with this assessment of correct bonding
of a wet niche fixture.