emiller233
- pittsburgh, pa
- Controls-Automation engineer
we got a very expensive custom Siemens motor that we wanted to verify wiring on before we tried to start it. the nameplate just says 460 Y (see picture of nameplate).
just wanted to make sure we should wire it as Y, not a start-delta setup?
the motor has been derated for 50Hz, so the top nameplate is the standard nameplate, and the bottom one is the new derated nameplate that we should be following
its a 6-lead motor
SIMOTICS SD MOTOR TYPE:
1CV3280B Low-voltage motor, IEC Squirrel-cage rotor, self-ventilated, IP55
60 Hz, P60: IE2 4-pole * Size 280S, * 75kW (50 Hz) 86kW (60 Hz)
3 AC 50Hz 240VD/415VY * 3 AC 60 Hz 480 VY
3 PTC thermistors for disconnection (2 terminals)
its a 6-lead motor