chevyx92
Senior Member
- Location
- VA BCH, VA
Will need to tap buss bar of 2500A 208V main gear. Gear is old and only has (3) racking breakers and they are all used and can't reconfigure them. That's leaves us with tapping the buss bar. Only problem is we only need a 3P 200A feeder to a transformer. According to the 25FT tap rules, using tap conductors sized at 1/3 of ampacity, we would need parallel 600 kcmil CU with 350 CU EGC. How in the world would you terminate parallel 600 CU in a 200A 3P fused disconnect?! I say you can't, and probably can't terminate in a 600V 400A fused disconnect either! I need so opinions here. I would hate to have to set a 600A disconnect and then fuse it down but that may be the only way to do this? What do you think? Any other options?