How would you handle...

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
If you had a note like this and almost every receptacle was separate circuit and you were using MC cable? You would have to use #10 MC and not #12 even though they are just asking for neutral to be #10.
 

Attachments

  • Capture.JPG
    Capture.JPG
    113.2 KB · Views: 1
I would ask whether they mean the neutral of MWBCs that supply separate single-pole circuits (as opposed to a single multi-wire load).
 
One outlet on it's own circuit( 1p-20a breaker). no?

Sounds like a guess. :D

I don't know what it means which is why I would ask the question. Assuming you're correct why would you need a #10 neutral for a 20 amp circuit with a #12 ungrounded conductor?
 
Sounds like a guess. :D

I don't know what it means which is why I would ask the question. Assuming you're correct why would you need a #10 neutral for a 20 amp circuit with a #12 ungrounded conductor?

Not a guess based on drawings. Each receptacle( well 90% of them) has it's own circuit.
 
Not a guess based on drawings. Each receptacle( well 90% of them) has it's own circuit.

Still makes no sense why you would have a #10 neutral and a #12 ungrounded conductor in a 2 wire circuit. It's either a mistake or someone doesn't have a clue.
 
The supernoodle was in the coppercabals best interests....trade rags were lousy w/non linear loads and harmonic editorials a few decades ago

True RMS meters sold like hotcakes

But the world turned ,few jobs were spec'd out for it, and now were stuck with antiquated labels

~RJ~
 
Is this something bidding, or do you already have the project? I also don't understand why that note is in there, but smells like there's going to be a spec line or general project note not allowing MC cable if it's already this over-engineered and calling for about 150 dedicated recepts in a typical office space.
 
Still makes no sense why you would have a #10 neutral and a #12 ungrounded conductor in a 2 wire circuit. It's either a mistake or someone doesn't have a clue.

Old specs. is my guess.
some of the specs we get are out of the late 80's and early 90's.
 
Is this something bidding, or do you already have the project? I also don't understand why that note is in there, but smells like there's going to be a spec line or general project note not allowing MC cable if it's already this over-engineered and calling for about 150 dedicated recepts in a typical office space.

Bidding. MC is allowed.
 
Where is that post about, eng./contractors again?
would love to hear back on the RFI, "too late to change bid the documents!".
Then you come in thousands over and the lowballer gets the job and an extra!
 