I would ask whether they mean the neutral of MWBCs that supply separate single-pole circuits (as opposed to a single multi-wire load).
Good point. Also I never seen all receptacles in office space on separate circuits. About 150. odd.
Wait, does the panel schedule show 150 different circuits for receps ?
I would first ask them what is a "separate circuit outlet'?
One outlet on it's own circuit( 1p-20a breaker). no?
Sounds like a guess.
I don't know what it means which is why I would ask the question. Assuming you're correct why would you need a #10 neutral for a 20 amp circuit with a #12 ungrounded conductor?
Not a guess based on drawings. Each receptacle( well 90% of them) has it's own circuit.
Still makes no sense why you would have a #10 neutral and a #12 ungrounded conductor in a 2 wire circuit. It's either a mistake or someone doesn't have a clue.
Is this something bidding, or do you already have the project? I also don't understand why that note is in there, but smells like there's going to be a spec line or general project note not allowing MC cable if it's already this over-engineered and calling for about 150 dedicated recepts in a typical office space.