- Location
- Placerville, CA, USA
- Occupation
- Retired PV System Designer
The transformer will be, in effect, an unbalanced motor load, so I would multiply it by 1.732 when adding in its HP equivalent.For this equipment, the motors are wired as 3 phase and the heaters and transformer are single phase.....how does this effect my calculation?
Then instead of looking at the VA available for your single phase resistive loads, look at the maximum current on each pole from the 30A limit.
But if you multiply out the transformer, you end up with more than 10HP. <sigh>
The inrush current of the transformer will probably not be as great as that way of estimating gives you, so you may still be just fine.
How much power will you actually be drawing from the transformer secondary?
Can you make sure that the resistive loads are on different phases from the transformer?