I am monitoring the 7.5 for power.
I will need to climb the leg and walk the plank, again.
I will need to climb the leg and walk the plank, again.
Last edited:
We have two loads with different motors. The 5HP is too small and the 7.5 is to large. Simple, swap the motors.
We are monitoring the load of the 7.5 to determine just how "loaded" it is. (0-100%) I am using a simple current transducer and another vendor is using a "power monitor".
From what I can tell the average loaded current is 5.09 amps vs. an unloaded average of 4.37. This makes it very difficult for my equipment to notice the difference. The vendor using the power monitoring equipment is complaining of the same difficulty. A max load of 5.27 amp is well within the 7.6 FLA of a 5HP
@480.
What am I missing?