mbrooke
Batteries Included
- United States
- Technician
Kind of what I suspected. I have no experience with impedance grounded systems, but I do understand the concept of what is being done there. Then my mind got to wandering a little and I figured that one could still connect line to neutral loads and they would work, but if NEC allowed that it would probably want overcurrent protection on the neutral, which introduces other problems if you had a multiwire circuit involved and opened the neutral conductor. You also would need some method of detecting neutral to ground faults otherwise they would just bypass the grounding impedance.
Correct. To many issues that could come up. Even if its low impedance you could still have a phase to neutral fault cause a voltage rise on the non faulted phases and the neutral due to the limitation of fault current. P-N loads will be fried. Neutral could become grounded as well like you mentioned. And if its a high impedance type a phase to ground fault can cause the ground to rise well above the neutral in potential. Up to 277 on a 480 volt system, which would be a major hazard.