MechEdetour
- NY, USA
- Design Engineer
Hi.
Seems like my life is filled with never ending thought experiments on grounding, and now I've come across another.
I'm pretty well versed in HRG (high-resistance ground) systems and how they operate, but I found myself in a discussion the other day that left me questioning some things.
To put my thoughts into words:
During normal operation on an HRG system (let's assume a 480/277Y secondary), there is no current flowing through the neutral/grounding resistor. Ideally there would be some, but let's also assume the capacitive charging current is negligible, err zero. Now lets assume that the grounding resistor has failed open (from a failed resistor element per say).
The system would then behave like an ungrounded system, would it not?
On an ungrounded delta system, the first L-G fault inadvertently grounds the system, causing it to behave like a corner grounded delta. So on the first L-G fault the system continues to operate. Second L-G fault results in a L-L fault which is a problem.
Is there any reason this logic would be any different if the system has a 480/277Y secondary instead of 480V delta? My conundrum: If I have an ungrounded wye secondary, and A-phase shorts to ground, system would still continue to operate and the only difference would be that VB-Gnd and VC-Gnd would now be 480V instead of 277V right? Similarly to the delta system, second fault on the wye system would also result in a L-L fault.
During this aforementioned conversation, the other individual was telling me that in the event the resistor fails open on an HRG system, persons would be exposed to a shock hazard on the first fault if they came into contact with the faulted phase. Like if a motor winding failed and the case was at the "same potential" as the faulted phase. I don't see how this would be a shock hazard as I just look at it as an ungrounded system without the resistor in the circuit.
Can someone set me straight?