CHAPTER 3 – WIRING METHODS AND MATERIALS
(Add) 300.4.1 Drilling and notching.
(A) Structural floor, ceiling and roof members.
1) Solid sawn lumber. Notches in solid lumber joists, rafters and beams shall not exceed one-sixth of the depth of the member, shall not be longer than one-third of the depth of the member and shall not be located in the middle one-third of the span. Notches at the ends of the member shall not exceed one-fourth the depth of the member. The tension side of members 4 inches or greater in nominal thickness shall not be notched except at the ends of the members. The diameter of holes bored or cut into members shall not exceed one-third the depth of the member. Holes shall not be closer than 2 inches to the top or bottom of the member, or to any other hole located in the member. Where the member is also notched, the hole shall not be closer than 2 inches to the notch.
Exception: Notches on cantilevered portions of rafters are permitted provided the dimension of the remaining portion of the rafter is not less than 4-inch nominal and the length of the cantilever does not exceed 24 inches.
(2) Engineered wood products. Cuts, notches and holes bored in trusses, laminated veneer lumber, glue-laminated members or I-joists are not permitted unless the effects of such penetrations are specifically considered in the design of the member and permitted by the manufacturer.
(B) Studs. Any stud in an exterior wall or interior bearing partition may be cut or notched to a depth not exceeding 25 per cent of its width. Studs in nonbearing interior partitions may be notched to a depth not to exceed 40 per cent of a single stud width. Any stud may be bored or drilled, provided that the diameter of the resulting hole is no greater than 40 per cent of the stud