tkb Senior Member Location MA Apr 13, 2017 #21 hill900505 said: Sorry for the confusion, I meant 4CCC per phase, 4 sets of ABC phases and I used three conduits. Click to expand... What size are are conduits?
hill900505 said: Sorry for the confusion, I meant 4CCC per phase, 4 sets of ABC phases and I used three conduits. Click to expand... What size are are conduits?
J jaggedben Senior Member Location Northern California Occupation Solar and Energy Storage Installer Apr 13, 2017 #22 JFletcher said: I dont see where the OP said the eqpt needs a neutral, and isnt it permissible to run AAAA, BBBB, CCCC in 3 conduits? .... Click to expand... Only with non-ferrous raceways.
JFletcher said: I dont see where the OP said the eqpt needs a neutral, and isnt it permissible to run AAAA, BBBB, CCCC in 3 conduits? .... Click to expand... Only with non-ferrous raceways.
Smart $ Esteemed Member Location Ohio Apr 13, 2017 #23 jaggedben said: Only with non-ferrous raceways. Click to expand... ...and underground plus comply with provisions of 300.20(B).
jaggedben said: Only with non-ferrous raceways. Click to expand... ...and underground plus comply with provisions of 300.20(B).