Humidifier wire and breaker size

Status
Not open for further replies.

james2012

New member
Location
Ashburn, VA
I am installing an Aprilaire 800 humidifier.

The product allows for a range of input power.
I would like to use the highest setting, which is 240v @ 16amps

I would expect a dedicated circuit of 12 gauge wire on a 20amp breaker to be fine for this 16 amp continuous load, but the installation manual calls for 10 gauge wire and 25amp breaker.

Is it safe to install this to run at 16amps on my 12/20 wire/breaker? Or do i have to run it at the lower setting, of 11amps, as the manual states?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I am closing this thread, in accordance with the Forum Rules.

This site is designed for:

  • Contractors
  • Electricians
  • Engineers
  • Inspectors
  • Instructors
  • Other electrically related individuals


* This NEC Forum is for those in the electrical and related industries. Questions of a "How-To" nature by persons not involved in the electrical industry will be removed without notice.
If you feel this action to be in error, feel free to contact me via PM to explain.

A reminder to all members, if you see a questionable post, feel free to report it by clicking the
report-40b.png
button at the bottom left corner of the post.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
I am installing an Aprilaire 800 humidifier.

The product allows for a range of input power.
I would like to use the highest setting, which is 240v @ 16amps

I would expect a dedicated circuit of 12 gauge wire on a 20amp breaker to be fine for this 16 amp continuous load, but the installation manual calls for 10 gauge wire and 25amp breaker.

Is it safe to install this to run at 16amps on my 12/20 wire/breaker? Or do i have to run it at the lower setting, of 11amps, as the manual states?

Do what the manual states. Sure the math works for 16A and 12AWG but there is some reason they picked that size wire and breaker.
 

JFletcher

Senior Member
Location
Williamsburg, VA
Welcome

I am installing an Aprilaire 800 humidifier.

The product allows for a range of input power.
I would like to use the highest setting, which is 240v @ 16amps

I would expect a dedicated circuit of 12 gauge wire on a 20amp breaker to be fine for this 16 amp continuous load, but the installation manual calls for 10 gauge wire and 25amp breaker.

Is it safe to install this to run at 16amps on my 12/20 wire/breaker? Or do i have to run it at the lower setting, of 11amps, as the manual states?

What is the exact wording of the instructions? if it suggests or recommends #10/25A breaker, that's not the same as requires or 'must use'.

I found the instructions:

"With factory settings, the Steam Humidifier draws 11.5 amps +/- 10%. Use a minimum 20 amp dedicated circuit when installing to operate at
11.5 amps. The Steam Humidifier can be set to draw 16.0 amps +/- 10% by repositioning dip switch #1 on the control circuit board (see Figure
13). When set to 16 amps, use a minimum 25 amp dedicated circuit. For both applications, size wire according to local codes."

ftp://ftp.aprilaire.com/Fulfillment/Humidifiers/800-Series-Humidifier-Install-Instructions.pdf

Yeah, you'd have to use a 25 or 30A breaker, and since you cant run #12 to that in this case, you're stuck with #10 as well. 110.3(B).

That +/- 10% if + would put you at 17.6A maximum which is too high a continuous load on a 20A breaker.
 