HV Grounding(15kV systems)URGENT!!!!

Status
Not open for further replies.

bennie

Esteemed Member
Re: HV Grounding(15kV systems)URGENT!!!!

Give more details...Type and size of cable? MGN or ungrounded secondary supply?

Contact a customer service engineer at the local utility. Also call the nearest IBEW lineman local, for companies experienced in medium voltage installations.
 

rey-man

Senior Member
Location
New york
Re: HV Grounding(15kV systems)URGENT!!!!

its 1/c, 4/0, EPR insulated, 15kV, installed triplexed.
thanks for the help.
 

bennie

Esteemed Member
Re: HV Grounding(15kV systems)URGENT!!!!

The insulation is ethylene propylene rubber (EPR) Do the single cables have a concentric neutral around the insulation jacket?
 

rey-man

Senior Member
Location
New york
Re: HV Grounding(15kV systems)URGENT!!!!

you mean the copper shielding tape???
which neutral are you referring to?
 

gwz2

Senior Member
Location
Indiana
Re: HV Grounding(15kV systems)URGENT!!!!

For starter(s), see:

250 Part X.

250.180 " - - - shall comply with all applicable
provisions of preceeding sections of this article and with 250.182 through 250.190, - - -"

250 Part I & up.

250.4
250.134, especially 250.134(B).
250.122.

Some cables just have a minimum (size) of shielding which is nothing more than a static drain wire.

Others have an (equivalent) 1/3rd size of the phase conductor, so that grounding conductors on 3 of the phase Conductors equals a full size grounded conductor when terminated at each end of the cable run.

The above description is basic only.

Consult the cable manufacturer by e-mail.

[ June 11, 2003, 03:15 PM: Message edited by: gwz2 ]
 

bennie

Esteemed Member
Re: HV Grounding(15kV systems)URGENT!!!!

The highest distribution system voltage is 34.5 KV. This system uses cable with a concentric neutral.
Three phase loads the neutral is 1/3 size. Single phase loads the neutral is full size.
 

bennie

Esteemed Member
Re: HV Grounding(15kV systems)URGENT!!!!

To get back to your original question...The ground wire only needs to be #6 cu. to a rod or butt plate.
 