Re: HV Grounding(15kV systems)URGENT!!!!
For starter(s), see:
250 Part X.
250.180 " - - - shall comply with all applicable
provisions of preceeding sections of this article and with 250.182 through 250.190, - - -"
250 Part I & up.
250.4
250.134, especially 250.134(B).
250.122.
Some cables just have a minimum (size) of shielding which is nothing more than a static drain wire.
Others have an (equivalent) 1/3rd size of the phase conductor, so that grounding conductors on 3 of the phase Conductors equals a full size grounded conductor when terminated at each end of the cable run.
The above description is basic only.
Consult the cable manufacturer by e-mail.