1994 60 Amp breaker in main panel feeding SER AL going compressor. Currently wired with a 40A slow blow.
Compressor was upgraded to a more efficient unit. New efficient unit label:
Compressor: RLA - LRA = 21.2 - 96.
Minimum circuit ampacity 28A.
Max Fuse/Breaker HACR = 45A.
It seems that this compressor could be on a 30A breaker. If so, why not put run this circuit to a 60A subpanel, run the compressor on a 30 amp circuit from subpanel.
That would free some capacity for a mini split. If possible, what is the largest circuit for the mini split? (I assume 30 Amps)