what is the proper method when doing load calculations for HVAC in a commercial application. i have a plan reviewer that wants to see the justification for the loads. it is not as easy as just looking at the nameplate on the unit, where you have MOP and MCA. i typically use 440.22(B)1. i find these motor values on the data sheet of the unit, and also include heat strip if applicable, and plug that KW number into the total design load, i am using 220.18(A) for motor loads and 220.51 for heat load, as a basis for design, but do you or should you consider the AC compressor/motors a continuous load ? and therefore add the 1.25,. i cannot find a specific code reference in article 220 or 440 to state requirements