if the MCA is used to determine the actual load of the HVAC, in this case the MCA 38 amps, a 40 amp breaker will not suffice, unless i am missing something here.
The MCA figure already includes the 125% of largest motor safety factor. Also the motors are very unlikely to draw their FLA. Thus you will usually see actual load to be roughly 2/3 of the MCA.