220.3 references Art 440, section IV, which tells you the minimum ampacity (mca) required for branch circuit conductors.
In other words, the branch circuit load is calculated by the required branch circuit minimum ampacity.
David
I was so hoping you were wrong on this, but unfortunately for me you are not.
I am still not 100% onboard...like that matters...but I reached out to someone at NFPA and they took the time for telephone conversation.
If I am understanding what you stated and they confirmed if I have say 50 HVAC units all the same that have 80amps FLA and 100A MCA I need to account for 5000amps in my service size rather 4000 based on the FLA values.
He recognizes this builds in a 25% buffer even though this is NOT continuous load.
This same approach needs to apply to ALL individually fed motors which builds in another 25% buffer for total motor load.
Are you in agreement with these statements ?
The last MH book I have on "Understanding the Code" is a 2005 version. In discussion on 220 it stated motor load TOTAL on a service is 25% of largest + balance of all others.
Is this correct ? or as stated above ?
If this is correct, it seems the same logic could be applied to art 440.