HVAC disco

Status
Not open for further replies.

websparky

Senior Member
Location
Cleveland, Ohio
First time I have seen one of these!
switch-g.jpg
 
Re: HVAC disco

A three pole disconnect with no locknut on the conduit stub out?

I'm guessing you're referring to the switched EGC?
 
Re: HVAC disco

Some 1 phase elevators use a 3 pole diconect the GC on one pole it has something to do with keepin emergencey power off with the disco off
 
Re: HVAC disco

Well first off, the EGC needs to be bonded to the enclosure. But, that's easy.

OK, here is a clue:

This is for a typical air conditioning condernser unit. This could be allowed for other types of equipment but usually not condensing units.

Does this help?
 
Re: HVAC disco

Did you exspect to find fuses? Just guessing. :confused:

FWIW, I know you said that the Green is the EGC, but I have seen lots of old installations that used Green as an ungrounded conductor.
 