HVAC disco

Status
Not open for further replies.
Re: HVAC disco

This is an outdoor enclosure, the cover swings up, that is why it is not visible.

The gunk on the blades is normal (well at least for Square D). They even sell this stuff as a repair part.

The switch is "on" in the down position, because it looks like the blade carrier is broken. It appears that each blade is making a deifferent amount of contact. This is why Lock Out/Tag Out requires a voltage test as well as a visual test to determine de-energized equipment.
 
Re: HVAC disco

I also disagree: all three blades look closed (energized) to me, especially in a close-up in PSP.
 
Re: HVAC disco

Jim, I agree. The material is factory switch gunk. Looking closely, I noticed also that the blades do not appear to be engaging the same. It's hard to tell, looking from in front. It also looks as if the left blade is engaged, buried in switch gunk, while the other two contacts are visible. The fixed blades are recessed on the two right ones, while the left appears to extend all the way out to the edge of the plastic frame. Probably my imagination, but might be broken (as you said,) or it might be a 'make before' contact, as with a twist lock where ground engages before the power. In this case, the neutral before power legs?
 
Re: HVAC disco

Other than the problems already pointed out with the EGC and lack of bonding I have no idea what you are talking about.

I give up, we give up. Now tell us what the heck you are talking about.

-Hal
 
Re: HVAC disco

Gosh! I never thought it would go this far.

The switch is in the off position.
The gunk is lube.
The EMT locknut is missing.
The enclosure is not bonded.
The EGC will be switched.
Violation of: 250.104(B)
(B) Switches. No automatic cutout or switch shall be placed in the equipment grounding conductor of a premises wiring system unless the opening of the cutout or switch disconnects all sources of energy.
The condensing unit will still have the control voltage energized and with the switch in the open position the condensing unit will not be bonded. This would also create a touch potential difference.
 
Re: HVAC disco

Originally posted by websparky:
The condensing unit will still have the control voltage energized and with the switch in the open position the condensing unit will not be bonded. This would also create a touch potential difference.
How is it possible to create dangerous touch potential from a 24 volt control transformer? :confused: Where is a 24 volt control system required to be grounded/bonded? :confused:
 