I want to see what the min. size disconnect required would be for the HVAC system below. Not the unit has (2) 70HP compressors and (6) fans. I'm hoping a 200amp will work.
The nameplate on the unit states:
480v 3 phase 60 HZ
(2) COMPRESSOR MOTORS
Compressor RLA = 56.2
Compressor LRA = 283
(6) FANS
FLA= 2.1
Minimum Circuit Amps = 169.2
Maximum over current protection Amps = 200
I plan on using a 200amp I-line breaker, 3/0 copper THHN wire in 2" conduit and use a 200amp non-fused disconnect at the unit. Please advise if this falls within the code. I was looking over 440-11 but it's a little confusing.
Thanks!