rt66electric
Senior Member
- Location
- Oklahoma
Went on a trouble call.
200 amp main tripping on a all electric house.
Checked for the standard loose connections and signs of overheating.
After grilling the customer about usage and timing of tripping, I decided that it was probably a weak breaker? or overtaxed breaker tripped by (2) hot water tanks, well pump, well pump, well pump-heater, bath HVL, aircompressor, AND.. everything in the house on AND... 70 amps of electric heat,.
I took amp readings and found ........
The outdoor heatpump/resistance backup heat package unit is fed by a 2P 60 amp breaker and a 2P 30 amp breaker.
When the unit is on... the 2p 60 draws 45 amp ......and........ the 2p 30 draws 25 amp for a total of 70 amps....
THE BIG KICKER.... If I turn off the 2P 60 the 2p30 jumps to ---70 AMPS---
If I reverse and turn the 2p 60 on and the 2p30 off the load jumps to ----70 amps----
It is as if the two circuits are combined inside the unit and draws upon parallel wires of different sizes. This does not seem right to me.
I related this info and he understood the conflict but had no basis for reference to make a decision. He called the HVAC company and relayed the info.
The HVAC replied that this was Normal. and the panel box breakes are designed to trip if necessary..IF anything goes wrong.
I allways thought the circuits were independant from each other. The compressor/heat pump was on the 2p 30 and the dry resistance heat was on a seperate 60 amp relay.
Anybody know the proper set-up? :blink: :?
200 amp main tripping on a all electric house.
Checked for the standard loose connections and signs of overheating.
After grilling the customer about usage and timing of tripping, I decided that it was probably a weak breaker? or overtaxed breaker tripped by (2) hot water tanks, well pump, well pump, well pump-heater, bath HVL, aircompressor, AND.. everything in the house on AND... 70 amps of electric heat,.
I took amp readings and found ........
The outdoor heatpump/resistance backup heat package unit is fed by a 2P 60 amp breaker and a 2P 30 amp breaker.
When the unit is on... the 2p 60 draws 45 amp ......and........ the 2p 30 draws 25 amp for a total of 70 amps....
THE BIG KICKER.... If I turn off the 2P 60 the 2p30 jumps to ---70 AMPS---
If I reverse and turn the 2p 60 on and the 2p30 off the load jumps to ----70 amps----
It is as if the two circuits are combined inside the unit and draws upon parallel wires of different sizes. This does not seem right to me.
I related this info and he understood the conflict but had no basis for reference to make a decision. He called the HVAC company and relayed the info.
The HVAC replied that this was Normal. and the panel box breakes are designed to trip if necessary..IF anything goes wrong.
I allways thought the circuits were independant from each other. The compressor/heat pump was on the 2p 30 and the dry resistance heat was on a seperate 60 amp relay.
Anybody know the proper set-up? :blink: :?