HVAC / Electrical

Merry Christmas

FEDS79

Member
Location
California
Occupation
HVAC
Refrigerant line and electrical line can be ran in same roof flashing?
Nec 110.26(F)(1)(b)
AHJ decides?
Can there be a code violation?
 

FEDS79

Member
Location
California
Occupation
HVAC
AI Overview
Learn more

According to NEC 2017 Code Changes Chapter 3, raceways or cable trays containing electrical conductors can't contain any pipes, tubes, or other systems for air, gas, water, steam, drainage, or other services.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Refrigerant line and electrical line can be ran in same roof flashing?
Welcome to the forum.

I don't know what you mean by running lines in roof flashing.

A channel or tube to hide lines is not a raceway or cable tray.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
For flat roofs these are called pitch pockets and yes everything associated with the unit can go through the same penetration.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
Raceway's enclose conductors.

A sleeve, chase, etc. that contains a raceway (with conductors within) and refrigerant lines is no different than having same raceway and refrigerant lines in same stud bay in a wall.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
NEC definition of "raceway " and "enclosed " contradict allowance with refrigerant lines....
They do not because you're not installing the refrigerant lines within the raceway. The refrig lines and the electrical raceway are separate but run through the same pitch pocket penetration.
 

garbo

Senior Member
We were taught to try to keep conduits, sealtite, cables etc at least one inch from all foriegn pipe runs. A conduit in direct contact with a refrigerant line that could be hot exiting a hot roof might damage conductors inside of a conduit.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
We were taught to try to keep conduits, sealtite, cables etc at least one inch from all foriegn pipe runs. A conduit in direct contact with a refrigerant line that could be hot exiting a hot roof might damage conductors inside of a conduit.
so keep some separation within the sleeve or in this case pitch pocket.

refrigerant lines in this situation don't normally get hot enough to be a problem though. Line between compressor and condenser possibly could be, but that line is within the unit and not run between units in a typical split system.
 

Galt

Senior Member
Location
Wis.
Occupation
master electrician and refrigeration service tech.
If your liquid line is hot you need to clean your condenser.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
When cooling, like now, the liquid line at the AH is barely warm, and the suction line is very cold.

I thought the hot line meant that's how much heat was being removed from the airflow.
 