2 refrigerant lines run from the outside condenser to the inside mini split indoor unit on a typical system with one head. One is the suction line that runs about 40 degrees in cooling mode and the liquid line that runs about at the ambient outdoor temp (roughly)
When the system reverses (in a heat pump) now the bigger line that was the suction in cooling is now the compressor discharge line in heating and gets very hot. The indoor unit is now heating and the liquid line (small line) remains the liquid line although the flow in it is reversed.
When the system reverses (in a heat pump) now the bigger line that was the suction in cooling is now the compressor discharge line in heating and gets very hot. The indoor unit is now heating and the liquid line (small line) remains the liquid line although the flow in it is reversed.