Strathead
Senior Member
- Location
- Ocala, Florida, USA
- Occupation
- Electrician/Estimator/Project Manager/Superintendent
I have one chiller on a feeder marked minimum circuit ampacity 360.5 and MOCP of 500. Are these assumptions/calculations correct?
- Disconnect size, 600A disconnect is required because 115% of 360.5 is 415A over the 400A frame size
- wire ampacity is 125% time 360.5 or 450.6 amps. I don't see the standard "next higher breaker..." clause in 440.6 (A) so I am assuming that you must use a conductor that is over 440.6 amps. Is this correct? So you couldn't use one 600 CU THWN at 75 degrees, correct?