Upsizing is based on multiple factors, such as:
- The MCA is a minimum size; it's always OK to go bigger
True, but you are not required to go bigger that is a design choice.
- MCA is based on actual running load, not motor/load because mca is a UL driven calculation, not NEC calculation. Is it not based on maximum rated load of the compressor (comparable to what they call full load amps for motor circuits) plus full load amps of other motors, heat strips, other accessories that may be a part of the unit?
- I have never met a mechanical/HVAC engineer that supplies/buys what they initially told me; typical goes up
- During performance testing the HVAC may not supply the amount of air required and mechanical will change fans to increase airflow, thus MCA goes up.If you want to design it to cover that, then that is your choice. If I am asked to install a circuit to a unit it is usually getting MCA supplied to it, and maybe is upsized for voltage drop if deemed necessary. If they change their mind and want a bigger unit - why is that my problem? I get to sell them larger conductors and maybe raceway and do the job twice because of their mistake - not my mistake.
- Installation by Contractor may be such that cable derating is required due to elevated temperature; e.g. roof install
MCA needs to include any necessary adjustments per NEC.
- Don't have to worry about short circuit damage
Others have asked just what this is about as well.
From experience; it does provide a margin to cover the unknowns during detail design, especially since the electrical is last to finish, and we are often times having to make guesstimates to cover the indecisiveness of other disciplines, and thus helps keep me from having to explain to the Owner why he needs to give the Contractor a change order.
And nope, I don't say the NEC has to be met. The job has to be permitted, in doing so the AHJ/state takes care of the minimum safety requirements. If I want more than minimum, I provide the details.