spsnyder said:
The answer to your question about being able to convert from tonage to electric load is NO. You need to know the type of HVAC. If it's chilled water your electric load will be much less than converting from tons to btu/hr (12,000 btu/hr per ton) to watts (3.41 btu/hr per watt). If your AC portion is chilled water you only need a fan blowing across a coil. Look for the info off the unit.
Right - I was assuming the OP was talking about a direct expansion "freon" type unit.

Never thought a chilled water "fan coil" type.
 