I did read it.Please go to the link that I provided above. AND read it.
This is what I was looking for. ThanksWhy are you multiplying by 125%? This factor is already included in the MCA value. Now "nameplate" is a bad term when parts of the code book tell you to multiply it by 125%, because there can be many terms on a nameplate -- LRA, RLA, FLA, MCA.
Yup, the MCA already continuous the additional 25% so no further calculation is required. Take the MCA, then look up the minimum conductor size in 310.16 and you're good to go. The Max OCPD can be any size between the minimum and the Max OCPD listed on the nameplate.
Thanks also Rob.
I Get the "Wire to the minimum/ fuse to the maximum" line of thinking. It was never a question for me, what I was looking for ( and it was answered ) is When the MCA is given is that 125% in it.
The scenario usually goes like this, I am roughing in a house no one can tell me the A/C unit information, So I know by experience the Minimum wire size of the largest unit that will get put in is a #8. So I rough in with 8-2 NM . Then the units get installed and the MCA can be any where from 20 amp to 40 amp. I see no need to run from the disconnect on the wall with a #8 if the MCA is 20.5 amp, but I just want to be sure that I am not going one size to small with a #12