The UL Marking Guide for Electrical Heating and Cooling Equipment says:
[quote
17. BRANCH-CIRCUIT, SHORT-CIRCUIT AND GROUND-FAULT PROTECTION
Units required to be marked with a minimum circuit ampacity (see “Minimum Circuit Ampacity”)
are also required to show the maximum ampere rating of the short-circuit and ground-fault
protective device for each applicable circuit. These markings also conform with NEC® Section
430.7(D). They are computed in accordance with Section 430.53 and take into account any
remote loads used in the ampacity calculations. The branch-circuit, short-circuit and ground-fault
protection marking is included on the same label as the ampacity marking and is typically
identified as “Maximum Fuse Amps,” “Maximum Fuse or HACR Type Circuit Breaker Amps,”
“Maximum Fuse or Circuit Breakers Amps,” “Maximum Overcurrent Protection Amps” or their
suitable abbreviations.
There are several other situations when the maximum ampere rating of the short-circuit and
ground-fault protective device must be marked on the unit, even though a marking for minimum
circuit ampacity may not be required. Typical examples are overcurrent protection devices for
separate high voltage control circuits or transformers in the unit. These markings are identified in
the same manner as described above, but can be located on an attached wiring diagram (see
“Wiring Diagram”) or adjacent to the terminals or leads to which the supply circuit wires are to be
connected, rather than on or adjacent to the unit nameplate.
The markings for short-circuit and ground-fault protection always include some indication of the
type of protection device as well as the maximum current rating. This is significant since the
various types of devices recognized by the NEC® to provide this protection do not necessarily
provide the same level of protection for all units. Briefly, if the marking indicates:
1) Only “Fuse,” then only fuses are to be used;
2) “Circuit Breaker” and “Fuse,” then either fuses or circuit breakers
3) “Fuse or Circuit Breaker” or “Overcurrent Protection,” then fuses or any type of circuit
breaker (including “HACR Type”) may be used[/quote]
I see this marking guide as well as the label as both being 110.3(B) listing and labeling instructions.