HVAC Intermittent Problems
HVAC Intermittent Problems
If the OP wired and breakered the unit correctly and there are no issues between the breaker and the unit, there is a problem with the unit. Maybe just maybe, the breaker may have an issue.
There is a post or response I made somewhere on the forum about something of this nature. My background is I have a Masters License in HVACR and 30 years experience. These kinds of problems can be similar to auotmotive and can be hard even for well seasoned Techs to nail down. Taking a current reading on compressors on a quick service call may not necessarily be enough. A meter that can catch and record peak current is useful such as Fluke 87 series.
The case I am referring to was also 480V and there was an insulation fault on one of the line conductors in the service that was brought up through the unit blower section as they often times were on Lennox GCS series RTUs. I was watching this confounded unit running with the blower panel off, babysitting as we call it and saw an arc flash in the conduit. I had to force the repair electrician to also see it because he was unable to make a leap of perception that I knew what I was speaking about at the time. So afterwards I said again, re-pull the wire to the nearest junction or all the way home if necessary.
With that said there can be all manner of situations that can cause imtermittent faults that can indeed be hard to trace quickly. In some cases they have to be ruled out methodically by " isolation " methods, and inspecting unit wiring runs in detail. Isolation to mean ruling out which loads on board that are not at fault by various methods including shedding the suspected load when possible for a " time."
Starting with the basics, all contactors, relays, and terminations need to be looked at closely. This means all the way to the compressor terminals and so forth.
Cabinet wiring can and does wear out and fail, and can be close to ground but not in direct contact. Compressors that are in a stage of mechanical degradation can run for seemingly long periods of time before they develop secondary electrical failures. It can get time consuming. The trick is to break it down into pieces, working with the HVAC guy if necessary. In my case it was always me who had to find the root of the problem, and I had to " fix " it.