I have a unit with a heat kit strip 41.9/47.4  mca 45/50 mop
My question is what wire size would I need to feed this unit in aluminum?

Normally I use copper but it's too expensive and I heard this new aluminum is not so bad type se
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
Residential
I have a unit with a heat kit strip 41.9/47.4  mca 45/50 mop
My question is what wire size would I need to feed this unit in aluminum?

Normally I use copper but it's too expensive and I heard this new aluminum is not so bad type se

My suggestion, refer to the manufacturer's Installation Manual that will include more detailed information than just the equipment name plate.
Most HVAC manufacturers don't allow Aluminum.
 

number2

Member
Location
Nc
Occupation
Electrical
My suggestion, refer to the manufacturer's Installation Manual that will include more detailed information than just the equipment name plate.
Most HVAC manufacturers don't allow Aluminum.
Thank you for your response i will check it out. Ive seen a few times where they run aluminum wire to the disconnect then a whip containing copper to the unit.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Thank you. That's what I came up with looking into the code book. Since type se cable go off the 75c degree column. (Only 10 awg smaller goes off the 60c degrees column)
Yes if using SE cable you can use the 75° C ampacity. Just out of curiosity what voltage are you applying?
 