HVAC wire sizing NEC

Merry Christmas

electro7

Senior Member
Location
Northern CA, US
Occupation
Electrician, Solar and Electrical Contractor
Was wondering if #10 thhn or thwn conductors are okay feeding this HVAC equipment? Im used to sizing the wire according to the max fuse size of 40A, and that is what is protecting this unit, but was wondering about NEC motor load requirements.

Thanks ahead of time for the help.
e8b1302e8c91673b3b4aabb03b375191.jpg


Sent from my SM-S918U using Tapatalk
 
Another question: so you dont need to multiply the MCA by 1.25 for continuous load?

Sent from my SM-S918U using Tapatalk
 
On average, most all 14 SEER rooftop units use 1034 watts per ton. That metric can be used to get an idea of what to expect if you get a service call for a bid on power install for an RTU. Wire sizing, disconnect, etc.

This is a 5 ton unit, or possibly a 6 ton by manufacturer?
 