He stated that the MCA is 25 amps.
*cough*
He stated that the MCA is 25 amps.
Yes, but only after this feeder/branch circuit question arose, which is not a material issue.He stated that the MCA is 25 amps.
"But, how do it know?!"The conductors between the 30 amp OCPD at the panel and the 25 amp OCPD at the disconnect can be by definition (OCPD at each end) a feeder. That means that they need to be a minimum of 30 amps but if the 25 amp OCPD is supplementary (Article 100 definition post #16) then the branch circuit begins at the panel and the conductors only need to be sized according to the MCA of 17.2 amps.
He stated that the MCA is 25 amps.
Infinity meant that the MOCP is 25A. Which we did find out in post #6.No, his original post stated that it was 17.2A.
You're correct, thanks I'll fix it.Infinity meant that the MOCP is 25A. Which we did find out in post #6.
BTW, why does 430.63 use the phrase "not less than" and why doesn't that allow arbitrarily large OCPD? I assume that 430.62 is only for motor loads, so that it doesn't apply to a feeder supplying a motor and other loads.
Cheers, Wayne
You're correct I had the written wrong terminology. It should have said MaxOCPD is 25 amps not the MCA.No, his original post stated that it was 17.2A.
-Hal
I would run #12 for almost any residential A/C, even if code allows #14, in case a replacement needs it.
Agree. I even run # 10 if some hack later on decides to install a different equipment that’s not Hvac just because it has a 30 amp.
Sent from my iPhone using Tapatalk
I'd run #10 to a 30 amp disconnect and all the way to the unit.
Unlike some "hacks" that would run #14.
JAP>
#14 is legally aceptable because your equipment won’t pull more than 20 amps. It’s just like wiring any Motor.
Sent from my iPhone using Tapatalk
OK, I've pored over Articles 240 and 430 some and now realize the above is in error. My current understanding:I'm not following this emphasis on whether the conductors are feeders. If the OCPD does not exceed the MOCP, then a feeder supplying only one motor load/piece of HVAC equipment would be sized the same as a branch circuit, per my understanding of 430.62 (and as is only reasonable).
OK, I've pored over Articles 240 and 430 some and now realize the above is in error. My current understanding:
240.21 requires conductors to to be protected against overcurrent at their point of supply except under specified circumstances. [And the Article 100 definition of overcurrent covers both overload and SC/GF.] 240.21(F) says "Motor-feeder and branch-circuit conductors shall be permitted to be protected against overcurrent in accordance with 430.28 and 430.53, respectively." 430.53 covers the case of branch circuits, but 430.28 covers only "Feeder Taps," not the general case of a motor feeder.
The upshot is that a motor feeder must have its overload protection at its point of supply unless it qualifies under 430.28 or under one of the sections of 240.21. Unlike a motor circuit branch circuit, where the overload protection need not be at the point of supply, only the SC/GF protection needs to be.
So if the MOCP in the OP's example were 30A, then it would be necessary to treat the 25A fuses as supplementary protection in order to say that the branch circuit starts at the 30A breaker, to allow #14 conductors on the 30A breaker, with overload protection provided integral to the HVAC equipment. And as the MOCP is actually only 25A, that is not possible, the conductors from the 30A breaker to the 25A fuses are definitely a feeder, and must have their overload protection at their point of supply, or meet one of the requirements of 430.28 or one of the sections of 240.21.
Getting back to the OP, if the conductors from the 30A OCPD to the 25A fuses meet one of the tap rules (say the 25' rule), then they could be #14s, rather than #10s.
Cheers, Wayne
The 30A breaker effectively "kills" 240.4(G) for the entire run since the MOCP size is 25A. 240.4(G) would only apply from the fused disconnect to the unit.The sole intent of the 30 amp branch circuit is to feed the hvac system then it falls under 240.4G.
Sent from my iPhone using Tapatalk
Agreed. The branch circuit can not begin ahead of the MOCP.The 30A breaker effectively "kills" 240.4(G) for the entire run since the MOCP size is 25A. 240.4(G) would only apply from the fused disconnect to the unit.
Max ocpd is 25A. The fused disconnect has 25A fuse in it. The panelboard has 30A breaker feeding the fused disco.
Which has #14 awg?
25 amp fuse or breaker?
Sent from my iPhone using Tapatalk