Have a hydromassage bathtub install. It needs 2-20 amp circuits (1- each, circ pump, and heater).
The framework of the unit has a bonding lug. 680.74 talks about bonding parts together within the unit with an 8awg solid copper bonding jumper. It says that the bonding jumper is not required to go back to the panel board or service equipment.
The guy I’m working with wants to run an 8awg thhn wire back to the panel. Is this required?
I’m not sure what to do with this bonding lug?
Obviously there is going to be an EGC with the branch circuits.
Thanks
Thanks