Trevor I see your point and it does make sense to me .
It also makes sense to have the metal things with touch potential ,and I do consider the metal parts in contact with the circulating water in contact with me when I'm sitting in the tub, to have equipotential .
I also answered the original question as
(B) metal piping onthe tub that is in contact with the circulating water
and was wrong.
I know the folks who made up the questions could be wrong and all the folks who reviewed and approved the material, who are much like us , they like to read and pick apart this stuff too, in all 14 states could also have missed this "mistake" , but I'll be bonding the metal parts and metallic supply piping because they have touch potential .
Which of the following components of a hydromassage tub are required to be bonded together by a #8 AWG copper conductor?
A: Internal non-current carrying metal components of a listed double-insulated hydromassage pump
B: Metal piping on the tub that is in contact with circulating water
C: Metal piping that supplies water to the tub
D: Both b & c are correct
Metal piping systems that supply Hydromassage bathtubs must be grounded
Article 680.74 in the 2002 NEC? was changed by deleting wording that required listed double-insulated pumps to provide a ?means for grounding internal, non-accessible, non-current carrying metal parts.? This change was supported by comments that pointed out that the 2002 NEC? language was appropriate for swimming pool pumps which are not-double insulated. Requiring bonding of internal parts of listed double-insulated hydromassage pumps would violate their listing.
The change was unanimously approved because the panel believed that an increased level of safety was provided for these installations when listed double-insulated hydromassage pumps were connected to a power source by means of a three wire cord that included an equipment grounding conductor.
Choice B is incorrect
(d) is correct. The change in article 680.74 omitted the requirement for bonding internal components of listed double-insulated hydromassage pumps because this would violate the listing of the pump.