Originally posted by marc deschenes:
My point is the N.E.C. tries to avoid over loads
Not always, check out 230.90 Exception No. 3.
But that is obscure, something much more common is any multi receptacle circuit.
Any multi receptacle circuit can be easily overloaded regardless of the plug configuration.
Originally posted by marc deschenes:
210.23 States" in no case shall the load exceed the branch circuit ampere rating , An Individual branch circuit shall be permitted to supply any load for which it is rated...."
Exactly,
An Individual branch circuit shall be permitted to supply any load for which it is rated
The receptacle is not the load, the utilization equipment is the load.
Originally posted by marc deschenes:
This branch circuit is rated at 15 amps the device will accept a load in excess of that , This in my mind constitutes a case where the load is able to exceed the branch circuit rating.
Yes the load
could exceed the OCP just like the load on a multi receptacle circuit can exceed the OCP.
If we say that a 30 amp receptacle fed with a 15 amp OCP is dangerous than we would also have to say a multi outlet circuit is also dangerous as it too can be overloaded.
The only answer to that would be individual branch circuits to every receptacle.
I will leave you with this
90.1 Purpose.
(B) Adequacy. This Code contains provisions that are considered necessary for safety. Compliance therewith and proper maintenance will result in an installation that is essentially free from hazard but not necessarily efficient, convenient, or adequate for good service or future expansion of electrical use.
The code is for safety not convenience.