Mike I am saying that the 2011 NEC allows the busbar as a connection between panel for the tap conductor. Some believe it was not allowed and a split bolt must be used.
Mike I am saying that the 2011 NEC allows the busbar as a connection between panel for the tap conductor. Some believe it was not allowed and a split bolt must be used.
I do not have the 2011 so I can not debate this.
I do not have the 2011 so I can not debate this.
So I understand. Two 'main' panels side by side. Not connected physically.
We bond the two 'main' panels together at the grounded conductor?
I thought we were talking the GEC not grounded conductors. The picture had a 1/0 to the water pipe and a jumper between panels with a #4. This was not clear as an acceptable means until 2011 when it allows the busbar as a tap.
Yes. We are talking about the same picture. The #4 is attached to the grounded conductors. I say no.
Any problem with the left panel line/load nuetrals being on the wrong side?
Yes, since the service conductors do not carry the entire load of the service thenT.310.15(B)(6) does not apply. Where in the table does it allow for 2 sets of 2/0? It doesn't because you cannot control the diversity that is in dwellings when the load is split. 3/0 is needed.
busman...
this has been a highly debated subject since the onset of 310.15(B)(6)
As I recall, in the '08 Code, to try and soften the debate, the CMP used the singular word "feeder" to designate ONE supply. If the whole house load was fed by more than one service/feeder the 310.15(B)6) did not apply. That was a change from the '-5 Code and I'm pretty sure it went back to plural in '11. Mr Holt submitted changes to that effect.
To review the process one has to go back and look at the ROPs and ROCs.
I am of the opinion that if one is under '08 with two feeders, 310.16(B)(6) does not apply. That said, it is one of the most overlooked sections.
Thanks Gus-- for helping me out.
It has always been my interpretation, even before the NEC 2008 that the install needed 3/0 copper. For one , show me in T. 310.15(B)(6) what it states for a 400 amp service. I will save you the problem-- it states 400 kcm copper not 2- 2/0 copper conductors. IMO, it never allowed for 2 service entrance runs. The idea behind this is that residential loads are diversified however when you split the load into 2 sets of service conductors that diversity is gone.
I still have to respectfully disagree, unless you can explain to me why it was plural - feeder(s) - in the 2005 code.
Mark
We can argue this all day as we have in the past. Let me try again..
First off these are not feeders....Yes?
Secondly is the Table will not allow it or has no provision for this install.
I have not researched '11, but I'd told it went back to feeder(S).
Read above that where it says ...feeder conductors that serve as the main power feeder to each dwelling unit and installed in.......
IMO, they are talking about the feeders in a multifamily dwelling. In other wrds the feeder to each unit.
It also states it must be the main power feeder. How can you have more than one main power feeder-- it is singular. I also believe that 2008 just clarified what was stated in 2005. Not a change per se but a clarification.